    3818 ac compressor overheating-gctid818343

    My toward ac stopped working, compressor overheats and stops running leaving fan blowing warm air Need to know tipe of freon gas I can use to ad to the system and any info on this ac Thanks
    1989 3818 "MARECHIARO"
    Upper Chesapeake Bay

    #2
    How long does the compressor run before it shuts down? If it runs for only a minute or so its more than likely a bad run capacitor. Being low on refrigerant usually won't cause the compressor to over heat. The other problem that might cause it to trip on internal overload is a fouled condenser. Also check the sea strainer if its partially plugged that will cause low water flow.
    1988 Mainship 36 Sedan
    1995 2858
    1988 2655
    1987 2150
    Commercial/Industrial HVAC Service Tech.

    Comment


      #3
      The refrigerant type will be listed on the units data plate. If its older than 5 years more than likely it will be charged with R-22 if its a newer unit it will be 410-A or R134-A. I just priced R-22 for a chiller repair and dealer cost on a 30 pound can is $788.00. I would recommend to have a qualified technician check it out to make sure whats going on with it.
      1988 Mainship 36 Sedan
      1995 2858
      1988 2655
      1987 2150
      Commercial/Industrial HVAC Service Tech.

      Comment


        #4
        Thank you for the help, last year it was working somewhat but this year doesn't work at all it runs for about 3 minutes and shots compressor off I checked it the unit and the compressor gets very hot and causes the thermal switch on top of the compressor to trip off, how do I determine what type of freon it needs fi was to try to recharge it
        1989 3818 "MARECHIARO"
        Upper Chesapeake Bay

        Comment


          #5
          It is the original Marine Air unit of the front room,
          1989 3818 "MARECHIARO"
          Upper Chesapeake Bay

          Comment


            #6
            I do have few cans of r22 that I purchased last month from E bay .the unit has two port whit brass caps on it, one is labeled as a suction I suppose that's where gets charged, I am familiar with Automotive units
            1989 3818 "MARECHIARO"
            Upper Chesapeake Bay

            Comment


              #7
              It more than likely has R-22. The symptoms you describe its not likely to be low on refrigerant, It sounds like an electrical problem. Low refrigerant can cause compressor over heating but that usually occurs after a long run and after it shuts off with high suction super heat temps. I would start by checking all electrical connections and water flow.

              If those are good I would check the compressor start components such as the start and run capacitors and the start relay if so equipped.
              1988 Mainship 36 Sedan
              1995 2858
              1988 2655
              1987 2150
              Commercial/Industrial HVAC Service Tech.

              Comment


                #8
                I just hooked up the gauge and Freon can to the suction side but I didn't not punched the can it is still sealed and noticed the Gauge in about 3 minutes the needle goes all the way over to the max 360 degrees and the compressor shuts off also noted the water Cooling discharge coils are getting very hot
                1989 3818 "MARECHIARO"
                Upper Chesapeake Bay

                Comment


                  #9
                  If you have a set refrigeration gauges I would hook em up and check the pressures before adding refrigerant. Over charging a system is actually worse than under charging and can cause damage. Also make sure you have a temperature pressure chart and check your condensing water temps and evaporator entering air temps.
                  1988 Mainship 36 Sedan
                  1995 2858
                  1988 2655
                  1987 2150
                  Commercial/Industrial HVAC Service Tech.

                  Comment


                    #10
                    Check the high side pressure also.
                    1988 Mainship 36 Sedan
                    1995 2858
                    1988 2655
                    1987 2150
                    Commercial/Industrial HVAC Service Tech.

                    Comment


                      #11
                      I need to get adapters for my gauges lines and start allover again
                      1989 3818 "MARECHIARO"
                      Upper Chesapeake Bay

                      Comment


                        #12
                        Usually if the compressor heats up rapidly its an electrical or condenser/high side issue.
                        1988 Mainship 36 Sedan
                        1995 2858
                        1988 2655
                        1987 2150
                        Commercial/Industrial HVAC Service Tech.

                        Comment


                          #13
                          Have you made sure you have water flow?? If the coils are getting hot it almost sounds like your not pushing enough water through the system.
                          Charleston, S.C.

                          Comment


                            #14
                            If your condenser is overheating, check your temperature difference of the cooling water into and out of the condenser. Verify water flow out through the hull. If you have an infra red temperature sensor, check the freon temp inlet and outlet of the condenser and compare the difference. The gas outlet should be quite cool. I'm guessing you have a clogged or scaled up condenser.

                            From the original nameplate on my Marine Air Systems from 1989, it's R-22 in the unit. The 16,000 BTU aft unit has 16 oz for a charge.

                            James
                            1989 Bayliner 3888, 175 Hinos,
                            Hurth 630's Onan 8kw MDKD
                            Lowrance Electronics!
                            Boating on Georgian Bay & the North Channel
                            Completed the Great Loop 07/25/19
                            AGLCA #8340
                            MTOA# 7469

                            Comment


                              #15
                              If the 3818 is like the 32, there is a magnetic water pump near the strainer. If you have one, you can tell if this is the problem right away by putting your hand on it after you hear the compressor shut down. If it's hot, you have found the problem. The replacement is like 2- 3 hundy or you can take it apart and make sure the impellers are clear.

                              Again, assuming the systems are the same.