TOPIC: 3818 ac compressor overheating

3818 ac compressor overheating 23 Jul 2017 03:22 #1

  • N4618Q59
  • N4618Q59's Avatar Topic Author
  • Offline
  • New Member
  • New Member
  • STILL MUCH TO DO
  • Posts: 56
  • Thank you received: 0
My toward ac stopped working, compressor overheats and stops running leaving fan blowing warm air Need to know tipe of freon gas I can use to ad to the system and any info on this ac Thanks

Please Log in or Create an account to join the conversation.

1989 3818 "MARECHIARO"
Upper Chesapeake Bay
Last Edit: by N4618Q59.

3818 ac compressor overheating 23 Jul 2017 13:21 #2

  • RPrather
  • RPrather's Avatar
  • Offline
  • Senior Member
  • Senior Member
  • Mankato,Mn
  • Posts: 184
  • Thank you received: 37
How long does the compressor run before it shuts down? If it runs for only a minute or so its more than likely a bad run capacitor. Being low on refrigerant usually won't cause the compressor to over heat. The other problem that might cause it to trip on internal overload is a fouled condenser. Also check the sea strainer if its partially plugged that will cause low water flow.
The following user(s) said Thank You: mikecain@bellsouth.net

Please Log in or Create an account to join the conversation.

1995 2858 7.4 B2 (Present boat)
1988 2655 460 KC
1987 2150 5.0 Cobra
Commercial/Ind HVAC/R Service Tech.

3818 ac compressor overheating 23 Jul 2017 13:26 #3

  • RPrather
  • RPrather's Avatar
  • Offline
  • Senior Member
  • Senior Member
  • Mankato,Mn
  • Posts: 184
  • Thank you received: 37
The refrigerant type will be listed on the units data plate. If its older than 5 years more than likely it will be charged with R-22 if its a newer unit it will be 410-A or R134-A. I just priced R-22 for a chiller repair and dealer cost on a 30 pound can is $788.00. I would recommend to have a qualified technician check it out to make sure whats going on with it.

Please Log in or Create an account to join the conversation.

1995 2858 7.4 B2 (Present boat)
1988 2655 460 KC
1987 2150 5.0 Cobra
Commercial/Ind HVAC/R Service Tech.

3818 ac compressor overheating 23 Jul 2017 13:31 #4

  • N4618Q59
  • N4618Q59's Avatar Topic Author
  • Offline
  • New Member
  • New Member
  • STILL MUCH TO DO
  • Posts: 56
  • Thank you received: 0
Thank you for the help, last year it was working somewhat but this year doesn't work at all it runs for about 3 minutes and shots compressor off I checked it the unit and the compressor gets very hot and causes the thermal switch on top of the compressor to trip off, how do I determine what type of freon it needs fi was to try to recharge it

Please Log in or Create an account to join the conversation.

1989 3818 "MARECHIARO"
Upper Chesapeake Bay

3818 ac compressor overheating 23 Jul 2017 13:34 #5

  • N4618Q59
  • N4618Q59's Avatar Topic Author
  • Offline
  • New Member
  • New Member
  • STILL MUCH TO DO
  • Posts: 56
  • Thank you received: 0
It is the original Marine Air unit of the front room,

Please Log in or Create an account to join the conversation.

1989 3818 "MARECHIARO"
Upper Chesapeake Bay

3818 ac compressor overheating 23 Jul 2017 13:41 #6

  • N4618Q59
  • N4618Q59's Avatar Topic Author
  • Offline
  • New Member
  • New Member
  • STILL MUCH TO DO
  • Posts: 56
  • Thank you received: 0
I do have few cans of r22 that I purchased last month from E bay .the unit has two port whit brass caps on it, one is labeled as a suction I suppose that's where gets charged, I am familiar with Automotive units

Please Log in or Create an account to join the conversation.

1989 3818 "MARECHIARO"
Upper Chesapeake Bay

3818 ac compressor overheating 23 Jul 2017 13:49 #7

  • RPrather
  • RPrather's Avatar
  • Offline
  • Senior Member
  • Senior Member
  • Mankato,Mn
  • Posts: 184
  • Thank you received: 37
It more than likely has R-22. The symptoms you describe its not likely to be low on refrigerant, It sounds like an electrical problem. Low refrigerant can cause compressor over heating but that usually occurs after a long run and after it shuts off with high suction super heat temps. I would start by checking all electrical connections and water flow.
If those are good I would check the compressor start components such as the start and run capacitors and the start relay if so equipped.

Please Log in or Create an account to join the conversation.

1995 2858 7.4 B2 (Present boat)
1988 2655 460 KC
1987 2150 5.0 Cobra
Commercial/Ind HVAC/R Service Tech.

3818 ac compressor overheating 23 Jul 2017 13:54 #8

  • N4618Q59
  • N4618Q59's Avatar Topic Author
  • Offline
  • New Member
  • New Member
  • STILL MUCH TO DO
  • Posts: 56
  • Thank you received: 0
I just hooked up the gauge and Freon can to the suction side but I didn't not punched the can it is still sealed and noticed the Gauge in about 3 minutes the needle goes all the way over to the max 360 degrees and the compressor shuts off also noted the water Cooling discharge coils are getting very hot

Please Log in or Create an account to join the conversation.

1989 3818 "MARECHIARO"
Upper Chesapeake Bay
Last Edit: by N4618Q59.

3818 ac compressor overheating 23 Jul 2017 13:56 #9

  • RPrather
  • RPrather's Avatar
  • Offline
  • Senior Member
  • Senior Member
  • Mankato,Mn
  • Posts: 184
  • Thank you received: 37
If you have a set refrigeration gauges I would hook em up and check the pressures before adding refrigerant. Over charging a system is actually worse than under charging and can cause damage. Also make sure you have a temperature pressure chart and check your condensing water temps and evaporator entering air temps.

Please Log in or Create an account to join the conversation.

1995 2858 7.4 B2 (Present boat)
1988 2655 460 KC
1987 2150 5.0 Cobra
Commercial/Ind HVAC/R Service Tech.

3818 ac compressor overheating 23 Jul 2017 13:58 #10

  • RPrather
  • RPrather's Avatar
  • Offline
  • Senior Member
  • Senior Member
  • Mankato,Mn
  • Posts: 184
  • Thank you received: 37
Check the high side pressure also.

Please Log in or Create an account to join the conversation.

1995 2858 7.4 B2 (Present boat)
1988 2655 460 KC
1987 2150 5.0 Cobra
Commercial/Ind HVAC/R Service Tech.

3818 ac compressor overheating 23 Jul 2017 14:01 #11

  • N4618Q59
  • N4618Q59's Avatar Topic Author
  • Offline
  • New Member
  • New Member
  • STILL MUCH TO DO
  • Posts: 56
  • Thank you received: 0
I need to get adapters for my gauges lines and start allover again

Please Log in or Create an account to join the conversation.

1989 3818 "MARECHIARO"
Upper Chesapeake Bay

3818 ac compressor overheating 23 Jul 2017 14:05 #12

  • RPrather
  • RPrather's Avatar
  • Offline
  • Senior Member
  • Senior Member
  • Mankato,Mn
  • Posts: 184
  • Thank you received: 37
Usually if the compressor heats up rapidly its an electrical or condenser/high side issue.

Please Log in or Create an account to join the conversation.

1995 2858 7.4 B2 (Present boat)
1988 2655 460 KC
1987 2150 5.0 Cobra
Commercial/Ind HVAC/R Service Tech.

3818 ac compressor overheating 23 Jul 2017 14:31 #13

  • Sportscar
  • Sportscar's Avatar
  • Offline
  • New Member
  • New Member
  • Posts: 53
  • Thank you received: 8
Have you made sure you have water flow?? If the coils are getting hot it almost sounds like your not pushing enough water through the system.

Please Log in or Create an account to join the conversation.

3818 ac compressor overheating 23 Jul 2017 15:28 #14

  • MacPhid
  • MacPhid's Avatar
  • Offline
  • Premium Member
  • Premium Member
  • Posts: 368
  • Thank you received: 63
If your condenser is overheating, check your temperature difference of the cooling water into and out of the condenser. Verify water flow out through the hull. If you have an infra red temperature sensor, check the freon temp inlet and outlet of the condenser and compare the difference. The gas outlet should be quite cool. I'm guessing you have a clogged or scaled up condenser.
From the original nameplate on my Marine Air Systems from 1989, it's R-22 in the unit. The 16,000 BTU aft unit has 16 oz for a charge.

James

Please Log in or Create an account to join the conversation.

1989 Bayliner 3888, 175 Hinos,
Hurth 630's Onan 8kw MDKD
Lowrance Electronics!
MMSI
316030379
Boating on Georgian Bay

3818 ac compressor overheating 24 Jul 2017 04:23 #15

  • iceclimber
  • iceclimber's Avatar
  • Offline
  • Platinum Member
  • Platinum Member
  • Posts: 2011
  • Thank you received: 115
If the 3818 is like the 32, there is a magnetic water pump near the strainer. If you have one, you can tell if this is the problem right away by putting your hand on it after you hear the compressor shut down. If it's hot, you have found the problem. The replacement is like 2- 3 hundy or you can take it apart and make sure the impellers are clear.

Again, assuming the systems are the same.

Please Log in or Create an account to join the conversation.

Last Edit: by iceclimber.

3818 ac compressor overheating 26 Jul 2017 02:10 #16

  • davesisk
  • davesisk's Avatar
  • Offline
  • Premium Member
  • Premium Member
  • Posts: 386
  • Thank you received: 30
My 1989 Marine Air AC in the main salon of my 3818 started shutting off last summer, similar to this. Although there was still some water flow, it was constricted. I had just gotten the boat, so I had to poke around a bit to find the sea strainer (under the hatch in the main stateroom). The sea-strainer was almost totally clogged up, and a live crab had moved in. I set him free (I'm sure it was a pretty comical site with me running thru the cabin with one hand under the sea-strainer to try to not drip gunk everywhere, and one finger of the other hand trying to poke the crab back into the sea-strainer without him grabbing my finger...that would have been a youtube moment, methinks), cleaned the sea-strainer (attach one of those little keyring floats to it if you're hosing it off outside...drop it in the water without it and it's gone!), stacked 5-6 bromine tablets in the sea-strainer (at the recommendation of several of my dock neighbors)...voila. I clean that sea-strainer about every 10 days or so of run-time...seems to be necessary in my location.

Start with the easy stuff...check the sea-strainer if you haven't already.

Cheers,
Dave

Please Log in or Create an account to join the conversation.

3818 ac compressor overheating 26 Jul 2017 13:07 #17

  • JonW
  • JonW's Avatar
  • Offline
  • New Member
  • New Member
  • Posts: 43
  • Thank you received: 7
Hot water discharge indicates not enough water flow as above, and also the unit has enough refrigerant in it to make the condenser discharge hot. Clean the water circuit but be prepared for a possible compressor failure in the near future once you get it going.